Q#1 Fault Analysis GATE EE 2008 MCQ +2 marks -0.66 marks

Consider a power system shown below:

Given that:

The positive sequence impedances are  and

3-phase Base MVA = 100

Voltage base = 400 kV (Line to Line)

Nominal system frequency = 50 Hz

The reference voltage for phase ‘a’ is defined as

A symmetrical three phase fault occurs at centre of the line. i.e. point 'F’ at time . The positive sequence impedance from source  to point 'F' equals 0.004+ j0.04pu. The waveform correspond phase 'a' fault current from bus X reveals that decaying dc offset current is negative and in magnitude at its maximum initial value. Assume that the negative sequence impedances are equal to positive sequence impedances, and the zero sequence impedances are three times positive sequence impedances.

The RMS value of the ac component of fault currentwill be

3.59 kA

5.07 kA

7.18 kA

10.15 kA

Explanation Locked!

Unlock this branch to view the explanation, track, bookmark and more.

Sign in to Unlock
Browse Practice Questions by Chapters / Topics in Browse Practice Questions by Chapters / Topics in GATE Electrical Engineering
Total Questions

Attempted

% Attempted

Correct

% Correct

Topic Questions Attempted Correct
Network Analysis 260 0 0
Signals and Systems 165 0 0
Control Systems 258 0 0
Analog Electronics 184 0 0
Digital Electronics 148 0 0
Electrical Machines 392 0 0
Power Electronics 237 0 0
Power Systems 344 0 0
EMFT EE 107 0 0
Measurement 158 0 0
Engineering Mathematics 225 0 0
General Aptitude 211 0 0