Q#1 Load Flow Analysis GATE EE 2023 MSQ +1 mark -0 marks

The bus admittance  matrix of a 3-bus power system is given below.

Considering that there is no shunt inductor connected to any of the buses, which of the following can NOT be true?

Line charging capacitor of finite value is present in all three lines.

Line charging capacitor of finite value is present in line 2-3 only.

Line charging capacitor of finite value is present in line 2-3 only and shunt capacitor of finite value is present in bus 1 only.

Line charging capacitor of finite value is present in line 2-3 only and shunt capacitor of finite value is present in bus 3 only.

Explanation:

Sum of the elements in a row of YBUS matrix represents the admittance b/w particular bus & ground.

Based on values above the system can be represented as,

π-model of a transmission line can be shown as

That is the line has equal capacitances at both ends.

So, we can consider line connecting bus-2 & 3 only has line charging capacitance of j0.5

Bus-3 has shunt capacitor of j0.5

∴ Statement b & d are correct & statement a & c are incorrect.

Browse Practice Questions by Chapters / Topics in Browse Practice Questions by Chapters / Topics in GATE Electrical Engineering
Total Questions

Attempted

% Attempted

Correct

% Correct

Topic Questions Attempted Correct
Network Analysis 208 0 0
Signals and Systems 21 0 0
Control Systems 18 0 0
Analog Electronics 10 0 0
Digital Electronics 138 0 0
Electrical Machines 17 0 0
Power Electronics 17 0 0
Power Systems 18 0 0
EMFT EE 8 0 0
Measurement 6 0 0
Engineering Mathematics 27 0 0
General Aptitude 104 0 0