The single line diagram of a lossless system is shown in the figure. The system is operating in steady-state at a stable equilibrium point with the power output of the generator being
, where
is the load angle and the mechanical power input is
. A fault occurs on line 2 such that the power output of the generator is less than
during the fault. After the fault is cleared by opening line 2 , the power output of the generator is
. If the critical fault clearing angle is
radians, the accelerating area on the power angle curve is ________times
(rounded off to 2 decimal places).

Assume maximum power transferrable before the fault

Before fault the system is operating under steady state so 



After fault clearance,




Accelerating area = Decelerating area (by equal area criterion)
Decelerating Area